News:

  • October 18, 2026, 08:08:51 AM

Login with username, password and session length

Author Topic: BRX Com issues  (Read 12701 times)

mhw

  • Hero Member
  • *****
  • Posts: 250
BRX Com issues
« on: July 22, 2021, 10:55:27 AM »
I have a BX-DM1E-36AR3 PLC. Connected to the Ethernet port are three BX-DMIO-M-D expansion modules, an HMI, and it is all connected to the facility network. Most times I am unable to connect to it with the programming software. The PLC MAC address will show up in NetEdit but the type is unknown and the IP address is 0.0.0.0. There are four other PLCs including an H2-DM1E that will continue to show in NetEdit. The HMI will continue to communicate and the PLC program is working. The only way that I have found to connect consistently is to disconnect the cable that is going to the facility network. After 30 seconds are so it will connect. Everything will work fine after I get connected and plug all of the Ethernet cables back in. When I am online there are no dropped packets and only a few retries in the IO monitor. Scan time is under 1ms.
Where do you think the problem is?

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6177
  • Yes Pinky, Do-more will control the world!
Re: BRX Com issues
« Reply #1 on: July 22, 2021, 11:34:10 AM »
I have a BX-DM1E-36AR3 PLC. Connected to the Ethernet port are three BX-DMIO-M-D expansion modules, an HMI, and it is all connected to the facility network. Most times I am unable to connect to it with the programming software. The PLC MAC address will show up in NetEdit but the type is unknown and the IP address is 0.0.0.0. There are four other PLCs including an H2-DM1E that will continue to show in NetEdit. The HMI will continue to communicate and the PLC program is working. The only way that I have found to connect consistently is to disconnect the cable that is going to the facility network. After 30 seconds are so it will connect. Everything will work fine after I get connected and plug all of the Ethernet cables back in. When I am online there are no dropped packets and only a few retries in the IO monitor. Scan time is under 1ms.
Where do you think the problem is?

What version of firmware is the BRX running?
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

mhw

  • Hero Member
  • *****
  • Posts: 250
Re: BRX Com issues
« Reply #2 on: July 22, 2021, 11:54:29 AM »
Quote
What version of firmware is the BRX running?
OS: 2.8.4
Booter: 1.0.10

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6177
  • Yes Pinky, Do-more will control the world!
Re: BRX Com issues
« Reply #3 on: July 22, 2021, 12:10:33 PM »
OS: 2.8.4
Booter: 1.0.10

Update to 2.8.6 please. There was a bug we fixed that was causing broadcast storms, which might be the issue here. It it's still an issue after updating, we'll dig further.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

mhw

  • Hero Member
  • *****
  • Posts: 250
Re: BRX Com issues
« Reply #4 on: July 22, 2021, 12:16:12 PM »
Quote
Update to 2.8.6 please. There was a bug we fixed that was causing broadcast storms, which might be the issue here. It it's still an issue after updating, we'll dig further.
Thanks Bob.....Where do I find 2.8.6?

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6177
  • Yes Pinky, Do-more will control the world!
Re: BRX Com issues
« Reply #5 on: July 22, 2021, 12:19:42 PM »
Quote
Update to 2.8.6 please. There was a bug we fixed that was causing broadcast storms, which might be the issue here. It it's still an issue after updating, we'll dig further.
Thanks Bob.....Where do I find 2.8.6?

Easiest way is to run DmD while connected to the Internet, so live update can pull it down automatically. Barring that, you can download it from either Host or ADC websites.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

mhw

  • Hero Member
  • *****
  • Posts: 250
Re: BRX Com issues
« Reply #6 on: July 22, 2021, 12:30:30 PM »
I didn't see it listed on either web site but the live update worked.
Thanks

Mike Nash

  • Hero Member
  • *****
  • Posts: 655
Re: BRX Com issues
« Reply #7 on: July 22, 2021, 03:35:21 PM »
Please refresh my memory on how to tell which versions of firmware are already on my computer without being connected to a PLC.

Most of the time if I am on site I don't have an internet connection.

Thanks.

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3850
    • Host Engineering
Re: BRX Com issues
« Reply #8 on: July 22, 2021, 04:00:40 PM »
Browse to your Public Documents Folder\Do-more\Designer2_8\bin\images\<part number>
example:
C:\Users\Public\Documents\Do-more\Designer2_8\Bin\Images\BX-DM1x

mhw

  • Hero Member
  • *****
  • Posts: 250
Re: BRX Com issues
« Reply #9 on: July 23, 2021, 08:46:55 AM »
Thanks for your help. The problem turned out to be another device on the network that was on the same IP address. I had suspected this early on but it did not respond to a ping so I started looking for something more complicated. In retrospect the problem was very obvious.