When you say common grounds. My pump is powered by 120, and the plc is on DC. This should be ok right? It is also the only wiring. It goes straight to the pump from the plc.
Yes, of course, this is OK. I meant:
- GD1 (pump drive) is connected to GND (BRX serial port)
- Shielding (if any at this point) is grounded at one end only.
- 120-ohm termination resistor between A+ and B- (pump drive) and
RS-485 is selected in the BRX's
System Configuration with the
Enable 120 Ohm Termination checked.
Granted, if you are just testing, and the cable is short, then the shielding and the termination are not critical at this point. If you have anything else wired up on the pump drive's terminals, the grounds on those may come into play. You might want to unhook everything else and just work with the communications first.