News:

  • October 17, 2026, 03:20:19 PM

Login with username, password and session length

Author Topic: PLC deleting folders  (Read 10037 times)

PLCwannabe

  • Hero Member
  • *****
  • Posts: 208
PLC deleting folders
« on: April 16, 2021, 12:27:27 AM »
The attached plc keeps deleting folders that are created on the ram-based file system. I recreate them every day, next day they're gone. Is there a fix for this issue?

RBPLC

  • Hero Member
  • *****
  • Posts: 586
Re: PLC deleting folders
« Reply #1 on: April 16, 2021, 07:27:59 AM »
I've noticed sometimes that if I go into the file system a file won't show up until I refresh.

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3850
    • Host Engineering
Re: PLC deleting folders
« Reply #2 on: April 16, 2021, 09:22:49 AM »
I've noticed sometimes that if I go into the file system a file won't show up until I refresh.
Yes, the Browse PLC File System dialog is not like Windows Explorer where files refresh automatically.  You must always hit the refresh button to re-read the directory.  Think of it more like ftp software (batch reads/writes), not Windows Explorer (live update).

PLCwannabe

  • Hero Member
  • *****
  • Posts: 208
Re: PLC deleting folders
« Reply #3 on: April 16, 2021, 09:34:43 AM »
I have tried refreshing, doesn't help. The files are actually gone, because I'm getting "unknown filelogging error".

Bolt

  • Hero Member
  • *****
  • Posts: 598
Re: PLC deleting folders
« Reply #4 on: April 16, 2021, 12:44:36 PM »
I always have to hit Browse to Root, even though I have no subfolders on @RAMFS.

PLCwannabe

  • Hero Member
  • *****
  • Posts: 208
Re: PLC deleting folders
« Reply #5 on: April 16, 2021, 03:12:17 PM »
Are there any situations where these files could get deleted, say when making certain configuration changes and then downloading? I have been tweaking this project almost daily, and I have had to recreate the folders at least 4 or 5 times.

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3850
    • Host Engineering
Re: PLC deleting folders
« Reply #6 on: April 16, 2021, 03:18:20 PM »
The RAM drive probably does get reset after a sysconfig download, possibly a program mode download of the program.  Runtime edit of the control logic would not reset the RAM drive.

Bolt

  • Hero Member
  • *****
  • Posts: 598
Re: PLC deleting folders
« Reply #7 on: April 16, 2021, 05:12:12 PM »
The RAM drive probably does get reset after a sysconfig download, possibly a program mode download of the program.  Runtime edit of the control logic would not reset the RAM drive.

I have found all of the above to be true.  The RAM is also cleared if you HALT a Program that is stuck continually looping reading a RAM file ::)  This may have something to do with a watchdog error, either way, not recommended ;D