No standard, but you have the right idea.
You could put DST22 (current time as 1970 Epoch value, the number of seconds since Jan 1, 1970) into first 2 WORDS of a PLC's PEERLINK block (e.g. PL0/1 as PL0:SD, PL16/17 as PL16:SD, PL 32/33 as PL32:SD, etc.).
What's good about DST22 as the "heart beat", is that it is a numeric value, not a bit, so there's no chance of hitting some "resonating" flaky comm sequence where the single bit stays ON for 5 cycles (and reports a false "dead PLC").
If it's changing, you know that PLC is alive and well (i.e. in RUN mode), so if it hasn't changed for 5 seconds, you know it's not.
Use a Delta contact with inline NOT contact driving a TMR 5.000s. If the .Done bit turns ON, that PLC has not reported a time change in 5 seconds.
STRDLT PL0:SD
NOT
TMR T0 5000
A side effect of this specific mechanism is that everyone can see the status of the Real Time Clock in all the other PLCs, if needed!