Author Topic: Can't Reset ST152 $IOError From Ladder  (Read 6497 times)

Mike Nash

  • Hero Member
  • *****
  • Posts: 655
Can't Reset ST152 $IOError From Ladder
« on: April 29, 2020, 09:43:57 AM »
H2-DM1E
Do-more v2.7.0
OS 2.7.3
Booter 3.0.8
FPGA 3.8
Hardware 7E


The issue is when I have an open Thermocouple on a T1F-14THM, I get ST152. When I reconnect the T/C, I can not get ST152 to clear. Everything else is fine, but I have to open I/O System View in DmD to get that cleared. I don't even have to do anything else, just open it. I did get it to clear by unplugging the ethernet cable to the EBC100 and putting it back.


I have tried a RST ST152 in the ladder, It doesn't care. I have tried MOVE $EthIOMaster,SlaveErrors $EthIOMaster.ResetSlaveStatus. It doesn't care.


I have 2 H2-DM1Es running standalone but talking one to the other to be sure it and its T1H-EBC100s are OK. Nobody gets faulted due to I/O loss, the checking is done in the program. There are multiple drops and main power sources for remote I/O.


Everything is cool except for ST152.


I don't have any$EthIOMaster.SlaveErrors (or Slave0Error, etc.) But I do have $EthIOMaster.SlaveWarnings = 1.


Help?

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3852
    • Host Engineering
Re: Can't Reset ST152 $IOError From Ladder
« Reply #1 on: April 29, 2020, 12:37:14 PM »
Try
MATH $EthIOMaster.ResetSlaveStatus "$EthIOMaster.SlaveErrors | $EthIOMaster.SlaveWarnings"
instead of MOVE of just the $EthIOMaster.SlaveErrors
to reset it on any Error or Warning (note the single pipe, not double pipe - single pipe does a bit-wise OR, double pipe is LOGICAL or - you want bit-wise).

Mike Nash

  • Hero Member
  • *****
  • Posts: 655
Re: Can't Reset ST152 $IOError From Ladder
« Reply #2 on: April 29, 2020, 01:01:29 PM »
Thank you,


I'll give it a try... And it works! Thank you, thank you.