How do i fix this. all have the same IP right?
See atached.
Thanks!
It appears you are using a hard IP address for one of the Modbus instructions, then use a variavle D0 for all the others. If these are all the same slave, i.e D0, once set, is not changing berween instructions, you can definitely ignore thse. Just right click on the Program Check rule and select Ignore in Rung, or even Ignore in Project if this is going to be utilized with the same IP address in all other new MxX instructions.
If, however these are different IP addresses, i.e. They are all different slaves, then ADC Product Engineer's post should be considered.