Author Topic: Analog Channel Failure  (Read 7977 times)

PLCwannabe

  • Hero Member
  • *****
  • Posts: 208
Analog Channel Failure
« on: February 11, 2020, 12:21:42 PM »
I'm trying to set up BRX for 4-20 milliamp sensor. As soon as i set the configuration to 4-20ma, I get a channel failure alarm. (see attached) when I set it to any other configuration( 0-10v, 0-5v) the warning disappears. I did hook up a 4-20 ma sensor to see if warning will disappear, the channel doesn't work, warning is still there. What could be the problem?

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6172
  • Yes Pinky, Do-more will control the world!
Re: Analog Channel Failure
« Reply #1 on: February 11, 2020, 12:23:15 PM »
I would stick a VOM in the circuit and see how much current it flowing through it.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

ADC Product Engineer

  • Hero Member
  • *****
  • Posts: 270
Re: Analog Channel Failure
« Reply #2 on: February 12, 2020, 07:56:10 AM »
If the channel is configured for 4-20ma, it must have a 4-20ma device wired to it or it will give an error.   That's just how 4-20ma works.  If it isn't in range, it is considered to be failed.

PLCwannabe

  • Hero Member
  • *****
  • Posts: 208
Re: Analog Channel Failure
« Reply #3 on: February 12, 2020, 09:13:41 AM »
Ok you guys were right. The sensor is actually a 3-wire type. I've only used  2-wire sensors before. I just assumed that the channel failure without a sensor hooked up meant a module problem.