News:

  • October 10, 2026, 05:23:27 PM

Login with username, password and session length

Author Topic: DoMore BRX comm to AB Controllogix with ethernet IP  (Read 7903 times)

jwbaker3

  • Hero Member
  • *****
  • Posts: 144
DoMore BRX comm to AB Controllogix with ethernet IP
« on: December 13, 2019, 10:05:43 AM »
What is the best way to message data between a BRX and a Controllogix with Ethernet? Both on the same subnet.

Thanks,
JW

ATU

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 2126
  • YKPAIHA
    • ATU, Inc.
Re: DoMore BRX comm to AB Controllogix with ethernet IP
« Reply #1 on: December 13, 2019, 10:18:37 AM »
Use the Explicit Message Server.

jwbaker3

  • Hero Member
  • *****
  • Posts: 144
Re: DoMore BRX comm to AB Controllogix with ethernet IP
« Reply #2 on: December 16, 2019, 08:40:42 AM »
Thanks for the reply. I already know this, I have used DoMore's to talk to many other pieces of hardware with Ethernet IP but never an AB Controllogix. I am look for an example of how to set up the AB and the DoMore. I tried to get the AB to talk to the BRX but had comm failures. I am sure it is a setup problem.

Thanks,
JW

ATU

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 2126
  • YKPAIHA
    • ATU, Inc.
Re: DoMore BRX comm to AB Controllogix with ethernet IP
« Reply #3 on: December 16, 2019, 10:39:58 AM »
Attached is a module for setting up the MSG instruction for a CLX

jwbaker3

  • Hero Member
  • *****
  • Posts: 144
Re: DoMore BRX comm to AB Controllogix with ethernet IP
« Reply #4 on: December 20, 2019, 09:50:21 AM »
Thank you for the example, just what I needed. I could not see the forest for the trees..

Thanks again!!!
JW