Mikek
Newbie
Posts: 9
TMRA and Variables
«
on:
November 18, 2019, 05:00:33 PM »
I am trying to use a V address IE V400 to set a preset for a TMRA. I get unreliable operation and a 6 digit value displaying as the preset with a 3 digit value in the V address. Must a K value be used with TMRA?
Thank you.
Logged
plcnut
Hero Member
Posts: 803
Re: TMRA and Variables
«
Reply #1 on:
November 18, 2019, 09:55:15 PM »
TMRA uses two consecutive V memory locations. If you entered V400, then it is using V400-V401.
Logged
Circumstances don't determine who we are, they only reveal it.
~Jason Wolthuis
Premier Systems Integration, LLC
http://premiersi.com
ADC Product Engineer
Hero Member
Posts: 270
Re: TMRA and Variables
«
Reply #2 on:
November 19, 2019, 07:18:57 AM »
Also depending on the model of the PLC, V400 might be in use by a system construct such as a timer or a counter.
Logged
Mikek
Newbie
Posts: 9
Re: TMRA and Variables
«
Reply #3 on:
November 20, 2019, 12:48:48 PM »
Thank you.
The PLC is a D0-06AR.
Logged