News:

  • November 23, 2026, 07:11:34 AM

Login with username, password and session length

Author Topic: pid set point  (Read 11425 times)

maciek

  • Sr. Member
  • ****
  • Posts: 95
pid set point
« on: March 28, 2019, 09:15:41 PM »
what is the best or easiest way to change the set point on a pid loop using a  hmi c more using brx plc

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3856
    • Host Engineering
Re: pid set point
« Reply #1 on: March 29, 2019, 09:11:15 AM »
Are you using the Do-more Symbolic Driver?  You will need to export all the symbols from Designer (File->Export->Element Documentation...
Make sure you pick C-more driver WITH STRUCT FIELDS (3rd radio button), and CHECK the Also export USED elements which do not have nicknames below that radio button.

If you are using the regular driver, it only understands basic built in types (e.g. X, Y, C, R, D, etc.).  You would need to utilize an R register for your HMI to write to (say R42), then have a
MOVE R42 MyPID.SP
box.