Imemotor:
Try importing this program, It should do just what you described. As far as the C-more is concerned whenever you program your panel you need to map V200 as your pointer for system temperature, and V201 as the pointer for pressure. You can also set pointers for all your Setpoints to v210-V213, the default values are loaded on the first scan, but you can adjust them accordingly when you program. Hope this helps, let me know if you have any more questions, and please feel free to critique my program, there are probably a lot of you guys that could do a lot better than me. Jason
PLC 05
// Rung 1
// Address 0
ISG S0
// Rung 2
// Address 2
ANLGIN K0 K0 K2 K0 V200
// Rung 3
// Address 40
STR SP0
LD K1000
OUT V210
LD K3000
OUT V211
LD K4000
OUT V212
LD K200
OUT V213
// Rung 4
// Address 49
STR X0
SET S1
OUT Y0
// Rung 5
// Address 52
STR X0
ANDN V201 V213
SET S5
// Rung 6
// Address 56
STRN X0
RST S1 S5
// Rung 7
// Address 59
SG S1
// Rung 8
// Address 61
STR V200 V210
JMP S2
// Rung 9
// Address 64
SG S2
// Rung 10
// Address 66
OUT Y1
OUT Y2
// Rung 11
// Address 68
STR V200 V211
JMP S3
// Rung 12
// Address 71
STRN V200 V210
JMP S1
// Rung 13
// Address 74
SG S3
// Rung 14
// Address 76
OUT Y1
OUT Y3
// Rung 15
// Address 78
STR V200 V212
JMP S4
// Rung 16
// Address 81
STRN V200 V211
JMP S2
// Rung 17
// Address 84
SG S4
// Rung 18
// Address 86
OUT Y1
OUT Y4
// Rung 19
// Address 88
STRN V200 V212
JMP S3
// Rung 20
// Address 91
SG S5
// Rung 21
// Address 93
OUT Y5
// Rung 22
// Address 94
END
// Rung 23
// Address 95
NOP
#BEGIN ELEMENT_DOC
"X0","On/Off switch","",""
"Y0","""System On""","","Indicator Light"
"Y1","Pump On","",""
"Y2","Fan speed 1","",""
"Y3","Fan Speed 2","",""
"Y4","Fan Speed 3","",""
"Y5","Alarm Output","",""
"V200","Channel 1","","Analog input"
"V201","Channel 2","","Analog input"
"V210","S.P. 1","",""
"V211","S.P. 2","",""
"V212","S.P. 3","",""
"V213","S.P. 4","","Low Pressure"
#END