Author Topic: BRX -> analog input module -> consistent measuring interval required  (Read 27220 times)

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6177
  • Yes Pinky, Do-more will control the world!
Re: BRX -> analog input module -> consistent measuring interval required
« Reply #15 on: April 18, 2018, 09:40:30 PM »
First page of the module config has a number of channels setting. You probably are set to 8, which means you are getting samples at ~45ms, well over the 2ms you would prefer.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

Zero Magnitude

  • Full Member
  • ***
  • Posts: 22
Re: BRX -> analog input module -> consistent measuring interval required
« Reply #16 on: April 19, 2018, 01:35:37 PM »
Didn't work.  The ISR is giving timeslices of 50,000us +/- a few us, but it's still giving bad info.  We're going to abandon this sensor and change to a completely different layout.  The accelerometer will still be used for spike measurement though.

This analog sensor is not part of the recall.