News:

  • October 22, 2026, 10:46:58 PM

Login with username, password and session length

Author Topic: Any way to record and playback analog  (Read 26010 times)

AustinT

  • Full Member
  • ***
  • Posts: 35
Any way to record and playback analog
« on: March 18, 2017, 06:19:21 PM »
Hi,  Is there a way to record an analog value ( kind of like the graph built in trend viewer ) and play the analog back to an output on command.

Thanks


BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6177
  • Yes Pinky, Do-more will control the world!
Re: Any way to record and playback analog
« Reply #1 on: March 18, 2017, 06:38:33 PM »
Depending on the required sample rate, it would be pretty easy to do that on a BRX with analog.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

AustinT

  • Full Member
  • ***
  • Posts: 35
Re: Any way to record and playback analog
« Reply #2 on: March 18, 2017, 07:57:23 PM »
Would it be possible to sample at 120hz?
What are the instructions/ steps to do this ?
I am trying to do a similar to this device
https://www.gilderfluke.com/index.php?main_page=product_info&cPath=1_2&products_id=130
Thank you

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6177
  • Yes Pinky, Do-more will control the world!
Re: Any way to record and playback analog
« Reply #3 on: March 18, 2017, 09:24:32 PM »
The speed is fine.

How many channels do you need?
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

AustinT

  • Full Member
  • ***
  • Posts: 35
Re: Any way to record and playback analog
« Reply #4 on: March 19, 2017, 01:19:42 PM »
Ideally 4 but at least 3
Thanks

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6177
  • Yes Pinky, Do-more will control the world!
Re: Any way to record and playback analog
« Reply #5 on: March 19, 2017, 02:57:50 PM »
Ideally 4 but at least 3
Thanks

BRX can easily do it, but it will be June/July before the analog output modules are out. For now, the BX-DM1E-36 has the most onboard analog, but there are only 2 onboard outputs channels.

We may also end up adding DMX512 as a protocol option between now and then. You didn't mention it, but it is something we have done in testing, and I would like to add both master and slave versions, and possibly even ArtNet.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

AustinT

  • Full Member
  • ***
  • Posts: 35
Re: Any way to record and playback analog
« Reply #6 on: October 21, 2017, 11:10:43 AM »
I would like to revisit this post now that tha analog cards have been released. What is the method to record and playback analog ?  Also was dmx512 implemented?
Thanks

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6177
  • Yes Pinky, Do-more will control the world!
Re: Any way to record and playback analog
« Reply #7 on: October 22, 2017, 02:20:41 PM »
I would like to revisit this post now that tha analog cards have been released. What is the method to record and playback analog ?  Also was dmx512 implemented?
Thanks

I'm pretty sure the FACTS analog modules are not fast enough to meet your requirement. The built-in channels are capable of nearly 1Khz, and I was of the understanding that they were targeting similar specs for the modules. Apparently not.

As for DMX, the current plan is to implement it in the BX-SERIO module. I have a software implementation for the internal port, but it takes some liberties that I would rather not put into product. By adding it to the BX-SERIO, we can implement it in hardware with no compromises.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

Evilbeard

  • Hero Member
  • *****
  • Posts: 160
Re: Any way to record and playback analog
« Reply #8 on: October 23, 2017, 07:47:11 AM »
I would like to revisit this post now that tha analog cards have been released. What is the method to record and playback analog ?  Also was dmx512 implemented?
Thanks

I'm pretty sure the FACTS analog modules are not fast enough to meet your requirement. The built-in channels are capable of nearly 1Khz, and I was of the understanding that they were targeting similar specs for the modules. Apparently not.

As for DMX, the current plan is to implement it in the BX-SERIO module. I have a software implementation for the internal port, but it takes some liberties that I would rather not put into product. By adding it to the BX-SERIO, we can implement it in hardware with no compromises.

So if I'm looking at the specs right, the Analog Input Expansion card has an update rate of 22.2Hz?

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6177
  • Yes Pinky, Do-more will control the world!
Re: Any way to record and playback analog
« Reply #9 on: October 23, 2017, 07:53:58 AM »
Yeah, that sounds correct.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

Garyhlucas

  • Hero Member
  • *****
  • Posts: 421
Re: Any way to record and playback analog
« Reply #10 on: October 23, 2017, 10:52:54 PM »
Facts built the BRX analog modules not Host?

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6177
  • Yes Pinky, Do-more will control the world!
Re: Any way to record and playback analog
« Reply #11 on: October 23, 2017, 11:55:53 PM »
Facts built the BRX analog modules not Host?

Correct. If there is enough interest in an analog module based on the built-in channel design (high-speed, universal voltage/current), we might look at Host doing a -3 expansion. We'll let the market drive that though.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6177
  • Yes Pinky, Do-more will control the world!
Re: Any way to record and playback analog
« Reply #12 on: January 08, 2018, 06:20:42 PM »
Also was dmx512 implemented?

Groovy...there are multi-colored lights flashing in my office right now...
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

plcnut

  • Hero Member
  • *****
  • Posts: 815
    • premiersi.com
Re: Any way to record and playback analog
« Reply #13 on: January 08, 2018, 06:35:16 PM »

Groovy...there are multi-colored lights flashing in my office right now...

Haven't got the Christmas lights taken down yet, eh? ;D
Circumstances don't determine who we are, they only reveal it.

~Jason Wolthuis
Premier Systems Integration, LLC
https://premiersi.com

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6177
  • Yes Pinky, Do-more will control the world!
Re: Any way to record and playback analog
« Reply #14 on: January 08, 2018, 07:09:49 PM »

Groovy...there are multi-colored lights flashing in my office right now...

Haven't got the Christmas lights taken down yet, eh? ;D

That would imply I got them up to start with.  ;)

But in case my subtle suggestion wasn't obvious enough, those flashing lights might be controlled by a BRX CPU via DMX512. ;D
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO