So far, my attempts at using the new subroutines have failed due to my wanting to put instructions there that are not compatible. Is there a list of instructions that won't work properly or at all in subroutines?

I am wondering if there is a better way to setup to do Modbus RTU read/writes to a large number of devices than an equivalent large number of MRX and MWX instructions and their associated elements. I am up to over 4000 documented elements and probably will have more to add as I get this firmed up.

Just for grins, lets say there are 50 devices (split over a pair of H2-SERIO-4s but just Port C on each SERIO is used.) That gives me 50 MRX and 50 MWX at a minimum. I don't think I see a way to use a single pair (times 2 for dual SERIOs) and index the parameters. The instructions actually do allow me to use indirect addresses for all but the success and error bits, but would it be legitimate to increment a pointer each time the success or error bit changes state?

I have already entered all of the preliminary descriptions and rungs at this point, but find I am wanting to modify some things and this means doing it manually 50 or 100 times. So is there an easier methodology with the current firmware/software (2.0.2/3)? I am not going to STAGE this simply because the actual rung count would grow a bunch and I am still up in the air on whether I find it more or less intuitive with STAGE.

The only interlocks I have are actually just "He's dead, Jim" 's so I skip them for xx seconds and then try again.

I don't want to make it hard to decipher for anyone following later though. The multiple instructions are pretty easy to understand.

Mike Nash

  • Hero Member
  • *****
  • Posts: 655
Re: MRX MWX Modbus RTU Strategy
« Reply #1 on: March 11, 2017, 11:17:49 PM »
Well, just playing in the simulator so I haven't gotten to actually try this part real world yet, but it looks doable. Indexed timers with indexed rung conditions aren't recommended! Indirect PD contacts get me a warning, but seem to work. Replacing it with a contact and Leading Edge Powerflow Modifier works with no warnings. The timer can get replaced with saving $UTC at edge and then MATH box IF'ing that with current $UTC for what I need.

So far it's looking more like 7 rungs PER SERIO for MRX and a few less than that for MWX since they share the Dead Jim handling. This versus 4 rungs PER MRX device address and 1 more PER MWX address.

It's a little less intuitive though. I did create some descriptively named memory blocks for the indexed status/control bits since the HMI won't need these.

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3853
    • Host Engineering
Re: MRX MWX Modbus RTU Strategy
« Reply #2 on: March 12, 2017, 08:36:55 AM »
Indirect PD contacts get me a warning, but seem to work. Replacing it with a contact and Leading Edge Powerflow Modifier works with no warnings.

Are you doing this using arrays to do edges?  If so, edge transitions are not going to behave like you think.  This is because the hidden edge state bit is NOT indexed like the element is.  However, you can create your own EDGE BIT data block EB and array index those and do edge contacts by hand.

// Is X ON THIS scan, but was OFF LAST scan EB, turn on C bit
STR X[V0]
ANDN EB[V0]
OUT C[V0]

// Save off state of X into EB for NEXT scan
STR X[V0]
OUT EB[V0]
« Last Edit: March 12, 2017, 08:38:54 AM by franji1 »

Mike Nash

  • Hero Member
  • *****
  • Posts: 655
Re: MRX MWX Modbus RTU Strategy
« Reply #3 on: March 12, 2017, 10:53:47 AM »
Indirect PD contacts get me a warning, but seem to work. Replacing it with a contact and Leading Edge Powerflow Modifier works with no warnings.

Are you doing this using arrays to do edges?  If so, edge transitions are not going to behave like you think.  This is because the hidden edge state bit is NOT indexed like the element is.

Yet it seemed to work. I am NOT looping however. This is all in MAIN and runs each rung in sequence. An index value is incremented and reset as needed, but only once per scan at most.

But I played some more with test logic and it does fail to work as anticipated at times. If I lock a bit on {V10=13 C[V10] C13 held true} then C14 is the bit that the LEPfM thinks is never changing although it is. This could certainly cause issues.

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3853
    • Host Engineering
Re: MRX MWX Modbus RTU Strategy
« Reply #4 on: March 12, 2017, 11:03:36 PM »
If you did all this in its own program code block and set all the V array indexes before the RUN, and EXIT when done, and monitor the program's .Done bit, you could use PD contacts in that program.  Then set the V array values for the next RUN from $Main, looking for .Done, ...

Mike Nash

  • Hero Member
  • *****
  • Posts: 655
Re: MRX MWX Modbus RTU Strategy
« Reply #5 on: March 13, 2017, 09:56:24 PM »
If you did all this in its own program code block and set all the V array indexes before the RUN, and EXIT when done, and monitor the program's .Done bit, you could use PD contacts in that program.  Then set the V array values for the next RUN from $Main, looking for .Done, ...

After getting all the rungs entered (did I really do that on my own time?!), I most likely will leave them as discrete instances. But if I have time with the hardware before it has to ship I hope to try an indexed version. Big if there on the time as always.

So which approach would be the snappiest? The scan time was already at 1.8mS before I even added all the add'l timers and success/fail counters (diagnostics). Granted this is not slow, but would indexed (NO loops) be faster due to reduced rung count or would the indexed elements make it a wash? Or?

I will not want to do it if it is too difficult to troubleshoot later on. I do like the layout you suggest.

Mike Nash

  • Hero Member
  • *****
  • Posts: 655
Re: MRX MWX Modbus RTU Strategy
« Reply #6 on: March 17, 2017, 10:15:02 PM »
If you did all this in its own program code block and set all the V array indexes before the RUN, and EXIT when done, and monitor the program's .Done bit, you could use PD contacts in that program.  Then set the V array values for the next RUN from $Main, looking for .Done, ...

I am not getting the hang of this at all. .Done is a tricky, tricky thingy, and so is RUN. I have attached a screenshot of my attempts to understand this.

1) If a Program has RUN at all, I cannot get it to restart using it's own .Done bit (program to run transition) because .Done is already on and I don't find any way to force it off. Hence the C0 logic in $Main Rung 3. C0 must be off to on for me to get TestProg to run again.

2) Similar issue in that .Done will never be seen as transitioning off to on if TestProg makes only one pass and exits. This is why TestProg Rung 2 has to be 2 scans to exit.

3) I don't see why I get D0 incrementing 3 for every 2 increments of D1. I have moved the RUN rung from the top of $Main to the bottom with no difference. The way I am reading the help, I think I should be scanning TestProg just as often as $Main but obviously it does not. Can someone straighten me out on the scan sequence there? I'm sure it has to be the EXIT but... My thinking is the EXIT should make the .Done true for the next $Main scan (because it had to go false after the first scan of TestProg) so it should just fall right in and run again, but it must not be. Stage gives me similar headaches.

Thanks.

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6177
  • Yes Pinky, Do-more will control the world!
Re: MRX MWX Modbus RTU Strategy
« Reply #7 on: March 17, 2017, 10:27:16 PM »
I will study when I have some time, but Stage is your friend. Seriously.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

Mike Nash

  • Hero Member
  • *****
  • Posts: 655
Re: MRX MWX Modbus RTU Strategy
« Reply #8 on: March 17, 2017, 11:01:45 PM »
I will study when I have some time, but Stage is your friend. Seriously.

Maybe I am just not responding to "tough love". I have a suspicion that whatever I am not seeing with the above example is related to my "Stage fright".

I do have a program running a machine using Stage, but it was more of a struggle than I liked.

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6177
  • Yes Pinky, Do-more will control the world!
Re: MRX MWX Modbus RTU Strategy
« Reply #9 on: March 17, 2017, 11:25:00 PM »
Maybe I am just not responding to "tough love". I have a suspicion that whatever I am not seeing with the above example is related to my "Stage fright".

Put the RUN immediately following a SG instruction, with no input logic. On the next rung following the RUN, use the .Done field to drive a JMP. The JMP can take you to another stage that will decide whether to run the program again (by jumping back to the stage with the RUN) or the JMP can jump right back into the stage you are already in (which will re-run the program). It'll work like a hose.

I do have a program running a machine using Stage, but it was more of a struggle than I liked.

DL stage or Do-more stage?
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6177
  • Yes Pinky, Do-more will control the world!
Re: MRX MWX Modbus RTU Strategy
« Reply #10 on: March 18, 2017, 09:25:19 AM »
Elaborating a bit more: whenever I find myself struggling to rearm something edge triggered, Stage always cures it. Maybe you don't think of such things as sequences, but they really are. You fire them, wait for an unknown time for completion, determine whether you want to run again, and repeat.

The reason I asked about DL vs Do-more on stage is that I think that DL stage can cause more trouble than it's worth. Stage is a tool. When it's the right tool, there is nothing better. Do-more's stage implementation allows you to use it only where it makes sense, but DL tends to be more all in. In Do-more I almost never use stages in $Main, but frequently do in program blocks. Even then, only when it's the right tool.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

Mike Nash

  • Hero Member
  • *****
  • Posts: 655
Re: MRX MWX Modbus RTU Strategy
« Reply #11 on: March 18, 2017, 10:17:16 AM »
I will skip the quotes. I have only used Stage in Do-more. It never seemed a good fit in my apps in DL.

I have to retract my statement anyway. I have not yet used it in a running machine. I have it running in a Do-more on my desk to do ASCII comms to a device.

I still don't follow the scan timing in my previous example.

I have attached another go at understanding this. The three possible choices for the EXIT are selected by C1, C2 OR C3 exclusively. C1 or C2 result in a D0/D1 result of 2.0 while C3 results in 3.0 - both are fewer increments than the 1.5 ratio of my Stage-less version. I'm not even sure why C3 works at all as it didn't without the Stage.

I also had it hang and fail to execute TestProg once after the switch to Stage, but I could not duplicate it. This is one of my hesitations.

Granted, I am doing something here that is not it's intended purpose (expecting it to execute TestProg every scan and increment) but I need to know WHY it does or doesn't work.

I suspect a subroutine would do exactly what I expect here, but the MRX, MWX are not welcome there so I would like to "get it" and be comfortable with the alternatives to straight ladder.

And on the edge triggered? CTAX... instructions gave me fits last year mostly due to failing to allow the instruction to complete before executing another (or the same one again). Lots was due to not figuring out the run to completion requirements along with the edge triggering, but maintaining, but... (Frankly I don't recall all the things I got hung on at the time. Our new BX-DM1E-36ED23 is in, but no time to play with it yet.)

Thanks for the help!

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6177
  • Yes Pinky, Do-more will control the world!
Re: MRX MWX Modbus RTU Strategy
« Reply #12 on: March 18, 2017, 11:03:06 AM »
I'm hearing two conflicting things: "every scan" vs asynchronous instructions like CTAXnnn and MRX/MWX. I'm confused about what you are wanting to do. If you want something every scan, use a subroutine. The reason certain instructions aren't allowed in subroutines is because they can't complete in a single scan. Since they are async, they need time to complete, and I'm showing you good techniques for managing that.

As for allowing completion of stuff in stages, that's why the stage transitions on Complete and Error are built directly into the async instruction. Use them and we do the work for you. That's essentially what I'm simulating with the RUN and .Done logic, which works beautifully. I know it does seem like tough love, and I'm really sorry. We harp on this ad nauseum...but when you use them like we intend, they work very well.

I wouldn't worry too much about the one-off failure you can't dupe. The ISG initialization needs a program to run transition, and I've confused myself a dozen times over stuff like that. One of the reasons I like to limit stages to outside $Main is that it ensures that proper initialization occurs when the program block is run. If for some reason I get the program block out of shape during development, I either use a HALT or kill it from the Project Browser.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

Mike Nash

  • Hero Member
  • *****
  • Posts: 655
Re: MRX MWX Modbus RTU Strategy
« Reply #13 on: March 18, 2017, 11:27:32 PM »
Just so you know there are no hard feelings, I have a functioning, indexed (not looping), dual SERIO Modbus RTU, built with programs running programs with Stages everywhere except $Main. And I did it on a Saturday for the educational value (since the discrete one was mostly done.)

I may never love these things (Stages), but considering the asynchronous instructions are "designed" to be used with Stage, I reckon I am going to have to learn to live with them. Yes, yes I can be stubborn to the point of my own detriment.

Scan time appears to be around an eighth of the time in the all discrete MRXs and MWXs version. There are 1/20th as many of each instruction. I won't know until all the slaves are up and talking (rather than just the one with the rest sitting in "time out" mostly) what the scan time will ultimately be. Understanding the indexing is harder, but editing time to add or change a feature is massively less.

And did you know a SETUPSER in the first rung of $Main wins out over any configs done in System Configuration or Dashboard? That took me awhile to find, after which I remembered putting it in the very first thing when I started. The Dashboard has quickly grown on me - I like it.

I would still like to know in the screenshots I posted previously WHY the counts increment as they do. At this point it is curiosity because it shows me I don't understand what is happening and there are no asynchronous instructions involved there.

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6177
  • Yes Pinky, Do-more will control the world!
Re: MRX MWX Modbus RTU Strategy
« Reply #14 on: March 19, 2017, 05:19:43 PM »
They aren't really designed for Stage, per se. They are designed to accommodate the special needs of async operations in sequential programming (with and without Stage), while Stage was designed to provide a good method for sequential programming. Used collectively, they work very well, and make most of the junk just disappear.

And that's the key. It works.

There is no right or wrong answer as long as you get it to work right. I only push this because I want you to have the very best experience with Do-more. As I have said many times: It's ADC's job to get you to buy the first Do-more PLC; it's my job to make sure you buy the second.

Looking at your program now...