News:

  • October 16, 2026, 09:59:58 AM

Login with username, password and session length

Author Topic: H0-ECOM Sending Out Too Many Braodcasts  (Read 36195 times)

tim s

  • Newbie
  • *
  • Posts: 6
H0-ECOM Sending Out Too Many Braodcasts
« on: January 24, 2017, 04:12:34 PM »
I have an H0-ECOM ethernet card installed on a DL06 PLC. My IT department is complaining because it is sending out too many broadcasts over the network. The IT person showed me a screenshot of Wireshark and sure enough it is the device in question. In 15 minutes it broadcasted 5 million packets. He also said maybe the ethernet card is going bad. My question is, is this the normal operation for this card? BTW, it does have the latest firmware version installed.

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3850
    • Host Engineering
Re: H0-ECOM Sending Out Too Many Braodcasts
« Reply #1 on: January 24, 2017, 04:33:08 PM »
You said ECOM (not ECOM100).  Are you doing any RX/WX instructions on the ECOM slot?  I believe it will send out broadcast packets for those.

tim s

  • Newbie
  • *
  • Posts: 6
Re: H0-ECOM Sending Out Too Many Braodcasts
« Reply #2 on: January 24, 2017, 04:36:55 PM »
There are no RX/WX commands being executed by the PLC.

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3850
    • Host Engineering
Re: H0-ECOM Sending Out Too Many Braodcasts
« Reply #3 on: January 24, 2017, 05:15:35 PM »
If you could send some of your wire shark traces to support@hosteng.com (maybe even just the screen shot you mentioned earlier), that would probably give us good info.

tim s

  • Newbie
  • *
  • Posts: 6
Re: H0-ECOM Sending Out Too Many Braodcasts
« Reply #4 on: January 25, 2017, 10:25:54 AM »
Message has been sent. Thank you.

PLCGuy

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 677
Re: H0-ECOM Sending Out Too Many Braodcasts
« Reply #5 on: January 25, 2017, 11:54:42 AM »
I would be interested in the results. And by the way, this is a good reason to have your own Machine Network. At our work, I am assigned couple hundred ip address on a separate machine network. We too had too much traffic on the network, and also, IT worried if there is a major crash of some sort, it will take down the whole network, so now we are separate.

tim s

  • Newbie
  • *
  • Posts: 6
Re: H0-ECOM Sending Out Too Many Braodcasts
« Reply #6 on: January 25, 2017, 01:32:12 PM »
That's a good point. I did recommend that about a year ago. It even says in some PLC docs to NOT connect to a business network.

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3850
    • Host Engineering
Re: H0-ECOM Sending Out Too Many Braodcasts
« Reply #7 on: January 26, 2017, 12:56:20 PM »
tim s,

Got your email and responded.  Please post here if you did not get my email.

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3850
    • Host Engineering
Re: H0-ECOM Sending Out Too Many Braodcasts
« Reply #8 on: February 03, 2017, 03:34:21 PM »
After talking with "Greg", it would appear that the PLC had ladder logic to send Report By Exception (RBE) packets, which are NOT broadcasts, but (are most likely) "normal addressed" IP packets.  But, if the ECOM module did NOT have Dip Switch 7 ON, the RBE mechanism would NOT be utilized, but instead would do the normal "directed broadcast" of a HAP protocol (DL ECOM) packet.  (RBE is designated in ladder program by using Address 90 in the RX instruction, and your V memory contains the IP packet address data in addition to any application data; the packets we saw were HAP protocol address 90, which is NOT a typical address, the address is usually 2, 3, 4, 5, 12, etc.).

If you just turn on Dipswitch 7 and keep your RX rung(s), I bet the broadcasts would go away.  Not only that, whatever server/database was getting those RBE IP data packets would start getting its data again.

I am not 100% sure this is the issue, but +90% sure.
« Last Edit: February 03, 2017, 03:36:18 PM by franji1 »