EDRV100, G soft and Modbus Address 48449-48465
« on: April 28, 2016, 06:24:53 PM »
The G-Soft help page has this, but it doesn't appear that G-Soft will work with a EDRV100 to communicate with a GS3 drive. (That would be a really nice feature)

PC to GS-EDRV Cabling
Please refer to the manual that came with your GS-EDRV for details regarding the GS-EDRV Ethernet connection.   Cable diagrams are shown on page 7 of the GS-EDRV manual.
Connecting a GS-EDRV to your network uses standard 10-Base-T Ethernet cables.   Like any device, the right type of Ethernet patch cable to use depends on whether you have a hub or not.


Also it appears that the EDRV100 can only read configuration data but not actual operational parameters like running voltage, current and frequency. (This would also be a nice feature to have)


Finally can I multi-drop more than one GS3 on an EDRV100?   

Thanks



Greg

  • HostTech
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 660
  • Hmmm...
    • Host Engineering, Inc.
Re: EDRV100, G soft and Modbus Address 48449-48465
« Reply #1 on: April 29, 2016, 12:33:53 PM »
Sorry but we don't write the GSOFT software.

Also, if you are using a Do-more CPU with an Ethernet port and you enable its Ethernet I/O Mastering capability and then obtain the the GS-EDRV100 as a slave, then those parameters are available either directly as structure members or as something you can query the drive using GSREGRD "GSEDrive Register Read" instruction. E.g...

Structure Members
  • $GS2_100.OutputFrequency
  • $GS2_100.OutputCurrent

Parameter Read with GSREGRD instruction
  • P21.03 Output Frequency
  • P21.04 Output Current
  • P21.05 DC Bus Voltage
  • P21.06 Output Voltage

etc.
There are two types of people in the world; those that can extrapolate from incomplete data sets.

Henryp

  • Hero Member
  • *****
  • Posts: 161
Re: EDRV100, G soft and Modbus Address 48449-48465
« Reply #2 on: April 29, 2016, 02:41:53 PM »
The GSREGRD list is missing Power factor angle. (P21.10) 

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3463
    • Host Engineering
Re: EDRV100, G soft and Modbus Address 48449-48465
« Reply #3 on: April 29, 2016, 03:50:12 PM »
The GSREGRD list is missing Power factor angle. (P21.10) 
Only available on GS2 or GS3.  Is not available on GS1 (unless there is new firmware).

Greg

  • HostTech
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 660
  • Hmmm...
    • Host Engineering, Inc.
Re: EDRV100, G soft and Modbus Address 48449-48465
« Reply #4 on: April 29, 2016, 04:28:28 PM »
Finally can I multi-drop more than one GS3 on an EDRV100?

No, one GS-EDRV100 per GS-drive.
There are two types of people in the world; those that can extrapolate from incomplete data sets.

Henryp

  • Hero Member
  • *****
  • Posts: 161
Re: EDRV100, G soft and Modbus Address 48449-48465
« Reply #5 on: May 02, 2016, 10:00:08 AM »
I'm talking to a GS3 and the GSREGRD list is missing Power factor angle. (P21.10) 

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3463
    • Host Engineering
Re: EDRV100, G soft and Modbus Address 48449-48465
« Reply #6 on: May 02, 2016, 10:46:01 AM »
I'm talking to a GS3 and the GSREGRD list is missing Power factor angle. (P21.10) 
I am guessing that the Do-more is mis-configured.  Check the Do-more I/O Configuration.

In System Configuration, dialog, in the tree, get to
I/O Configuration
Ethernet I/O Master
Your GS-EDRV100

You should see a GS3 like below, but I am guessing that it is currently configured as GS1.

To change the drive type, right click on the drive and the context menu should let you Select Drive Type (pick DURApulse GS3).

The GSREGRD instruction's register selection dialog should also show the Drive type.  The picture below shows the GSREGRD Read GS3 Register dialog box (note the title bar and the P21.10 entry).  A configured GS1 drive will NOT have the P21.10 entry in its dialog.