Author Topic: DL05 high speed input  (Read 34383 times)

sparky1234

  • Newbie
  • *
  • Posts: 5
DL05 high speed input
« on: March 12, 2008, 11:45:59 AM »
I'm new to the Automation Direct PLC's.  I need to measure the speed of a device that has a an output of 5VDC and a frequency of 0Hz-100Hz.  I'm not sure which mode would be best to chose.  Any help would be great.

Thanks

MikeS

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 270
    • Host Engineering, Inc.
Re: DL05 high speed input
« Reply #1 on: March 12, 2008, 03:37:46 PM »
before we press on with suggestions, are you planning to use the onboard high speed inputs? or using the h0-ctrio module?

if it's the onboard hsio inputs, you're probably better off posting on the automationdirect.com forum, as that is their hardware, not ours.

if it the h0-ctrio module, you're at the right place.
Good design costs a lot. Bad design costs even more.

sparky1234

  • Newbie
  • *
  • Posts: 5
Re: DL05 high speed input
« Reply #2 on: March 12, 2008, 03:46:28 PM »
Yes, I am using the onboard high speed inputs.  I believe I've got figured out now.  Sorry, I thought AD and Host eng. were one in the same.