1. Setup -> Panel Manager. Pick your driver, in this case AutomationDirect ECOM Ethernet and put the ECOM IP address in the field provided.
2. Create a few objects on your screen and assign them to the device that is attached to the ECOM driver. IF you just added a driver and did not delete the existing driver this will be "DEV002".
3. Send the Project to the Panel. At this point you want to select Ethernet and click Browse and find your panel. Then assign it an IP Address that is in the same subnet, but different from your ECOM IP Address. Download the project and you should be up and running.