Author Topic: Using modbus tcp through a ecom100  (Read 27872 times)

Bobby

  • Sr. Member
  • ****
  • Posts: 60
Re: Using modbus tcp through a ecom100
« Reply #15 on: September 29, 2016, 04:27:06 PM »
Success! Thank you again!

PLCGuy

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 677
Re: Using modbus tcp through a ecom100
« Reply #16 on: October 07, 2016, 11:41:16 AM »
Hi Greq, Just a comment on saying you would like us to use the on-board Ethernet on the Do-More.
The following is only when using external I/O. It is not a good idea to use the same port to program, have the HMI and external I/O. If the port crashes for some reason it is dangerous to have external I/O go down too. It just give a little more protection.
At least that was what I was always told. Is there any plans to make a similar Ecom for Do-More or just now thinking about it, use the ERM module. I think I just answered my own question.  ::)

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6179
  • Yes Pinky, Do-more will control the world!
Re: Using modbus tcp through a ecom100
« Reply #17 on: October 07, 2016, 11:47:07 AM »
The new platform has an option slot where the USB port currently is existing DM1x CPUs. There are a handful of port options for that including Ethernet. It isn't as fast as the internal Ethernet port, but more than adequate for programming and HMI. So yes, we do have a plan to make this easier.

On existing hardware, it would be preferable to use an H2-ECOM100 for programming and HMI and use the internal Ethernet port for I/O.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO