« on: January 02, 2015, 03:11:48 AM »
Hello,
Im having trouble with the net time instruction. I apologise if its been covered elsewhere, but i couldn't find much info.

So I've opened the udp port 123 on my router, but still the net time instruction reports an error.
I'll attach a screen shot of the logic, and id appreciate any suggestions.

Thanks



ADC Product Engineer

  • Hero Member
  • *****
  • Posts: 270
Re: NETTIME
« Reply #1 on: January 02, 2015, 12:28:28 PM »
That server seems to be offline at the moment.  Give 24.56.178.140 (WWV.NIST.GOV - Fort Collins, CO) a try.

Rastus81

  • Jr. Member
  • **
  • Posts: 15
Re: NETTIME
« Reply #2 on: January 02, 2015, 09:32:21 PM »
That server seems to be offline at the moment.  Give 24.56.178.140 (WWV.NIST.GOV - Fort Collins, CO) a try.

Thankyou for your help, but it didn't work. I have tried about 10 different servers.

ADC Product Engineer

  • Hero Member
  • *****
  • Posts: 270
Re: NETTIME
« Reply #3 on: January 03, 2015, 02:27:58 PM »
Are you triggering C24 each time you try to set the time?  The NETTIME box is a one shot box, so it has to see a rising edge on the input to fire off.

Also be sure that the Gateway portion of the Ethernet settings for your Do-more processor is pointing to your routers internal IP address.
« Last Edit: January 03, 2015, 02:30:05 PM by ADC Product Engineer »

Rastus81

  • Jr. Member
  • **
  • Posts: 15
Re: NETTIME
« Reply #4 on: January 03, 2015, 09:20:22 PM »
Also be sure that the Gateway portion of the Ethernet settings for your Do-more processor is pointing to your routers internal IP address.

Thankyou! This was the problem. My gateway was set to 0.
Domore support is second to none.

Regards
Rastus