News:

  • August 16, 2026, 04:25:33 AM

Login with username, password and session length

Author Topic: ecom 100 and password  (Read 33787 times)

Henryp

  • Hero Member
  • *****
  • Posts: 161
ecom 100 and password
« on: December 24, 2014, 02:10:03 PM »
I’m using Ecom 100 cards in various DL PLCs at our treatment plant. It appears that when a DL PLC program is password protected, the ability to write to a bit or boolean is lost. If I connect to the PLC with DS5 using a password or if I remove the password, the ability to write to the bit is restored. V memory locations seem to be unaffected and work ok. I can duplicated the issue using Kepdirect’s OPC server and quick client and with my SCADA software and its Modbus driver.

Controls Guy

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 3626
  • Darth Ladder
Re: ecom 100 and password
« Reply #1 on: December 24, 2014, 02:36:01 PM »
There's a secret handshake!   :D

There's some rule for creating a password that still allows comms.  IIRC, you have to start the password with an "A" to allow it.  If that's not it, it's something like that.
I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.

Controls Guy

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 3626
  • Darth Ladder
Re: ecom 100 and password
« Reply #2 on: December 24, 2014, 02:38:34 PM »
Or better answer.....just switch to Do-More!  Do-More allows enable/disable of all the various rights for each user class, so this isn't an issue, plus selective protection of individual code blocks.
I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.

plcnut

  • Hero Member
  • *****
  • Posts: 814
    • premiersi.com
Re: ecom 100 and password
« Reply #3 on: December 24, 2014, 03:55:27 PM »
CG, you are correct: The password must start with a capital 'A' to allow write access.
Circumstances don't determine who we are, they only reveal it.

~Jason Wolthuis
Premier Systems Integration, LLC
http://premiersi.com