Since you are running them continuously, that means that they re-arm immediately. That means that the OnSuccess and OnError bits will be on for 1 PLC scan. On the simulator, this is much faster than 1 ms, let alone the low probability that the Ladder View status communication request will be processed exactly on that 1 scan.
What I like to do in situations like this is use the INC box with a differential contact driving it. Actually, two of them, one that counts successes and one that counts failures/errors.
STRPD OnSuccessBit
INC D0 // OnSuccess count
STRPD OnErrorBit
INC D1 // OnError Count
Then, your incrementing status of D0 and D1 will give you good feedback as to the level of success and failure.