News:

  • June 28, 2026, 09:03:31 PM

Login with username, password and session length

Author Topic: Do more timer  (Read 7248 times)

azeotrope

  • Jr. Member
  • **
  • Posts: 10
Do more timer
« on: November 22, 2014, 04:39:16 PM »
I have noticed my timers are running 2x too fast. A tmr set for 30 sec runs 15 sec. What can cause this?

Thanks

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3827
    • Host Engineering
Re: Do more timer
« Reply #1 on: November 22, 2014, 05:17:05 PM »
Make sure you are only using a timer resource once, e.g. T0 - you should only have one timer instruction using T0.  Look in your Cross Reference view, or float your cursor over the timer in question and let the Cross Reference pop-up and see where the timer structure is being used as an OUTPUT or INPUT/OUTPUT (in/out).

You would also be seeing a Program Check Warning being logged at download time for duplicate timer structures being used (you can also run Program Check via the Online Toolbar or via the menu, PLC->Program Check).

azeotrope

  • Jr. Member
  • **
  • Posts: 10
Re: Do more timer
« Reply #2 on: November 23, 2014, 09:49:11 AM »
Yeah that was it, should have seen that. Thanks