News:

  • June 26, 2026, 01:16:43 PM

Login with username, password and session length

Author Topic: Peerlink  (Read 16984 times)

DLTimmons

  • Hero Member
  • *****
  • Posts: 232
Peerlink
« on: September 12, 2014, 03:41:08 PM »
Is there a way to make peerlink reject data from PLC out side of it subnet? I am working the first of 10 groups of 3-4 PLC's that need to talk with each other in that group but not direct with the other groups and the group need to communicate with a server over the shop network. Would be nice to have the address of each group set so that I can take a laptop and connect locally with any group and not have to hunt for IP address so I can connect. Of course you to make this connection with some thing when it's down and you have half of management there wanting to know when your going to have it running

Right now it looks like Modbus is the only way and keep the link to the server.

Donnie

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6161
  • Yes Pinky, Do-more will control the world!
Re: Peerlink
« Reply #1 on: September 12, 2014, 04:24:42 PM »
Unfortunately, no. PEERLINK uses straight broadcasts to make it simple and foolproof. We made an active decision to leave out the configurablility and addressibility to keep it that way. DLRX/DLWX would probably be the best choice.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

ADC Product Engineer

  • Hero Member
  • *****
  • Posts: 270
Re: Peerlink
« Reply #2 on: September 12, 2014, 04:38:26 PM »
If this were me, I would put in managed switches and separate the PLC groups on VLAN's.

DLTimmons

  • Hero Member
  • *****
  • Posts: 232
Re: Peerlink
« Reply #3 on: September 12, 2014, 04:50:24 PM »
If this were me, I would put in managed switches and separate the PLC groups on VLAN's.

Our IT group does not understand a machine environment and they want to control the network.

DLTimmons

  • Hero Member
  • *****
  • Posts: 232
Re: Peerlink
« Reply #4 on: September 12, 2014, 04:51:40 PM »
Unfortunately, no. PEERLINK uses straight broadcasts to make it simple and foolproof. We made an active decision to leave out the configurablility and addressibility to keep it that way. DLRX/DLWX would probably be the best choice.

I will use the Modbus TCP as that's the way the server will communicating with the PLC any way.

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6161
  • Yes Pinky, Do-more will control the world!
Re: Peerlink
« Reply #5 on: September 12, 2014, 05:11:22 PM »
Our IT group does not understand a machine environment and they want to control the network.

This conjurs memories of Mordac the Preventer of Information Services.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

DLTimmons

  • Hero Member
  • *****
  • Posts: 232
Re: Peerlink
« Reply #6 on: September 12, 2014, 06:21:10 PM »

This conjurs memories of Mordac the Preventer of Information Services.


Controlling data is one thing controlling a machine that can crash and damage it's self another ;D

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6161
  • Yes Pinky, Do-more will control the world!
Re: Peerlink
« Reply #7 on: September 12, 2014, 06:25:04 PM »

This conjurs memories of Mordac the Preventer of Information Services.


Controlling data is one thing controlling a machine that can crash and damage it's self another ;D

Indeed!
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

PLCGuy

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 677
Re: Peerlink
« Reply #8 on: September 16, 2014, 12:35:40 PM »
DLTimmons, check with your IT and see if they will give you a block of IP addresses. Out IT set up a machine network and gave us a block of addresses we control. We give them the info and they log it. The machine network has its own xxx.xxx.xxx.xxx. IT then gives us access to that network from any other work network. I can be at my office or on my notebook or in China and access that network. If the machine network goes down, it will not crash anything else. Works great. Sometimes IT departments can be hard heads and not willing to do this for you.

DLTimmons

  • Hero Member
  • *****
  • Posts: 232
Re: Peerlink
« Reply #9 on: September 16, 2014, 03:01:37 PM »
DLTimmons, check with your IT and see if they will give you a block of IP addresses. Out IT set up a machine network and gave us a block of addresses we control. We give them the info and they log it. The machine network has its own xxx.xxx.xxx.xxx. IT then gives us access to that network from any other work network. I can be at my office or on my notebook or in China and access that network. If the machine network goes down, it will not crash anything else. Works great. Sometimes IT departments can be hard heads and not willing to do this for you.

Years ago they gave us a block in the lower 100 address of 192.168.4.X then a about four years ago had us change to 10.1.0.X still the same lower 100 address. then two years ago had us change to 20.1.0.X and set it up on a v-lan. about 6 months ago they finally gave me a port in my office that I could connect to the 20.1.0 subnet with so I had to have a second Ethernet port on my desk top for that connection. Now we used the 100 address up and need more the problem is they have radios and switches on the up 150 address all over it and we have no ideal what address they have used. Part of the problem is we have had 4 different network admin's in the last 8 years each want to do things differently. We have close to 30 WinPLC's with about 12 on the network the rest are stand along. Now we are adding Do-mores with remote I/o and multiply PLC in groups.