Author Topic: Filter Display with Transducer input thru domore onto cmore screen  (Read 6284 times)

fluidpowerman

  • Full Member
  • ***
  • Posts: 21
I am using 4-20 mA pressure transducer inputs to my domore plc and viewing them on my cmore.  currently my display numbers bounce around between -2.00 and +2.00 on the display.  I have tried using the "first order filter" to nullify the readings to no avail.  I would appreciate any feedback on how I might be able to buffer it a bit so my number aren't jumping around and I can zero them out.

Thanks for the feedback

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6161
  • Yes Pinky, Do-more will control the world!
Re: Filter Display with Transducer input thru domore onto cmore screen
« Reply #1 on: July 23, 2014, 07:55:16 PM »
You can greatly increase the aggressiveness of the filter and it should smooth out.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

fluidpowerman

  • Full Member
  • ***
  • Posts: 21
Re: Filter Display with Transducer input thru domore onto cmore screen
« Reply #2 on: July 24, 2014, 12:38:39 PM »
Yes, It works great.  Thanks for the input :)