I am having the same problem with a H2-ECOM100 card locking up w/ the red error light on. This one has caused considerable heartburn, as it is a remote site that requires a 20 minute drive to get to.
A short system overview. Our Ethernet network contains one DL205 Master, one DL06 slave, one DL205 slave (the problem child), with a C-More HMI that is accessing data from the DL205 Master and the DL06 Slave. These items are all connected via individual cables to a common switch. The control room data that we need is pulled from the master, via Modbus radio, so the Ethernet network is local only. At one point we were talking RX/WX broadcasts, the old way, but I am now using a peer to peer table in the master PLC. I do notice a slight hesitation once in a while on the problem ECOM card, but can't nail it down to any specific event. If I pull either the DL06 or the C-more out of the network, the hesitation goes away. I don't know if this would have anything do do with the fault?
After going to your FAQ0045, I checked off what we are doing against your recommendations.
(1) We use Cat 5e jumpers and cables.
(2) Thinking that electrical noise might be an issue, we took a temporary cable directly out of the PLC cabinet door to our switch to minimize interference. The problem stayed with us.
(3) I was wondering what noisy I/O might be considered to be? We have a 260 CPU in slot 0, a D2-08ND3 input card in slot1, an F2-08TRS output card in slot 2, an F2-04AD-1 analog input card in slot 3, a F2-02DA-1 analog output card in slot 4, and the H2-Ecom100 Ethernet card in slot 5. All of the I/0 is 24 VDC with interposing relays for higher voltage loads. The PLC base is 24VDC.
(4) The ethernet cable was originally routed with other 24VDC wiring, but the solution in #2 above would have taken care of that.
(5) We have a ground wire pulled from my main service to a PLC cabinet grounding point. The PLC is grounded to this point.
I am assuming that line filters are not needed on a 24VDC base as the 24VDC power supply would act as a filter of sorts.
Looking back over our system trends, I noticed that the card faults only when the chlorine generation process is running, but is at very random intervals- 1 hour to multiple days.
There is a large DC rectifier cabinet mounted directly below the PLC cabinet. Would it be possible that the non-linear loads would affect this card, even though the wiring is not in close proximity to each other?
I also thought that heat might be an issue. The room gets up to 90 deg F at times, but this is well within specs.
Last, but not least. According to a further FAQ, it looks like there is no way to reset the ECOM but to cycle power?
If anybody has any suggestions, I would appreciate the input.