Author Topic: "Overrides" is greyed out -- Can't use?  (Read 3897 times)

axle_f

  • Newbie
  • *
  • Posts: 2
"Overrides" is greyed out -- Can't use?
« on: January 29, 2008, 03:38:03 PM »
When is the "overrides" normally available?  The 06 manual refers to just setting up bit overrides using the drop down menu.  I have not found a way to enable this feature?  In the meantime, for testing purposes I have to program a bit around my logic, or change the address to sp1 or sp2 to test the logic.

Any help would be appreciated.

Thanks

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3703
    • Host Engineering
Re: "Overrides" is greyed out -- Can't use?
« Reply #1 on: January 29, 2008, 03:44:44 PM »
Your CPU must support overrides (not all CPUs support them, check your PLC manual)
Your DirectSOFT link's protocol must support overrides.  K-Sequence supports overrides, but DirectNet does not.  Make sure your PLC serial port is configured for K-Sequence and make sure your Link is using K-Sequence.  If you are using an Ethernet link, make sure you are using K-Sequence or ECOM protocol (not the ECOM module, but ECOM protocol under the protocol tab).

axle_f

  • Newbie
  • *
  • Posts: 2
Re: "Overrides" is greyed out -- Can't use?
« Reply #2 on: January 29, 2008, 07:00:22 PM »
Thank you for the help.  This is/was the problem.  Do any of the manuals cover this?  I could not find it.