Could you comment on the following estimates of the situation:
1) If multiple axes are spread across multiple modules, I assume communication directly between the two modules will be necessary for coordinated motion. The update time per axis will presumably need to be much faster than maximum scan times in CPU's, so you can't use the CPU as an intermediary, and it would be an unreasonable hit to the CPU anyway,
and
2) I assume that if module to module communication is necessary then the 205 backplane is not an option. First, it was probably not designed with capability for module-initiated comms, especially ones directed not at the CPU but at another module (although the ECOM....). Then, even if module to module comms were theoretically possible, they would probably not be feasible on the scale needed for axis coordination.
Is that all about a reasonable assessment?