News:

  • October 28, 2026, 01:38:57 PM

Login with username, password and session length

Author Topic: WinPLC and DoMore  (Read 29717 times)

DLTimmons

  • Hero Member
  • *****
  • Posts: 232
Re: WinPLC and DoMore
« Reply #15 on: February 11, 2014, 03:16:49 PM »
Figured out the string their only 10 different string have them equate to a number like "MOVE"=2  and past an integer to the Do-More The guy that set this system like to use strings for a lot of things.

Can you use the H2-SERIO in a remote rack from what I could find it's no. If that is the case I will have to have 3 Do-Mores in the system What would be the better way to link them Peerlink or Modbus TCP?

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6179
  • Yes Pinky, Do-more will control the world!
Re: WinPLC and DoMore
« Reply #16 on: February 11, 2014, 03:27:21 PM »
You're correct, SERIOs in local base only.

Peerlink is fallin'-off-a-log easy, but is only about 100ms updates. Either MRX/MWX or DLRX/DLWX could potentially run north of 10ms. Any will work.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO