News:

  • October 28, 2026, 11:38:22 AM

Login with username, password and session length

Author Topic: Data from (2) DL06's to a Do-More  (Read 17832 times)

jwbaker3

  • Hero Member
  • *****
  • Posts: 144
Data from (2) DL06's to a Do-More
« on: November 22, 2013, 08:21:22 AM »
We build a multiplexer to read 128 thermocouples with one 4 channel thermocouple input card on the 06. I have 2 of these units installed (on this project) with the same program in both 06's so the V memory address in both are the same. The 06's are connected to the network with Ecom100 cards and I am using the Ethernet port in the Do-more cpu. I need to read the memory blocks from both 06's 1 time per minute (I don't think speed is a problem). With the DL205/260 cpu's I would map the ecoms peer to peer and read the data into the main plc to use it for control of the process, I have built a lot of the systems with up to 8 06's with 1 DL205/260 control plc. I really like the Do-more I have used it other projects but never this type, so what is the best way(s) to get the data into the Do-more?

Thanks
JW

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6179
  • Yes Pinky, Do-more will control the world!
Re: Data from (2) DL06's to a Do-More
« Reply #1 on: November 22, 2013, 09:51:08 AM »
Unless I'm missing something obvious here, just use DLRX like you would use RX (or the IBox) in the 260.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

Controls Guy

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 3628
  • Darth Ladder
Re: Data from (2) DL06's to a Do-More
« Reply #2 on: November 22, 2013, 02:10:43 PM »
All your bits are Modbus-compatible as both master and slave, so that's another option.   I've done Modbus/TCP between multiple DL-classic PLCs, and it works fine.
I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.

jwbaker3

  • Hero Member
  • *****
  • Posts: 144
Re: Data from (2) DL06's to a Do-More
« Reply #3 on: November 22, 2013, 03:24:37 PM »
Thanks for the replies. The DLRX is how I thinking to do it, I just wanted to make sure there was not a better (Doing-More) way, it never hurts to ask.

Thanks,
JW

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6179
  • Yes Pinky, Do-more will control the world!
Re: Data from (2) DL06's to a Do-More
« Reply #4 on: November 22, 2013, 04:59:28 PM »
There are definitely easier ways to share data in Do-more (PEERLINK is your friend), but the DLRX instruction is the best way to pull data from DL controllers with the minimum changes at the DL end.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

CReese

  • Hero Member
  • *****
  • Posts: 184
Re: Data from (2) DL06's to a Do-More
« Reply #5 on: November 25, 2013, 02:46:33 PM »
You mean I've been using MRX and address translation when DLRX was there the whole time? Sheesh.

CReese

  • Hero Member
  • *****
  • Posts: 184
Re: Data from (2) DL06's to a Do-More
« Reply #6 on: November 25, 2013, 03:35:22 PM »
I take it back. MRX is more flexible anyway. I don't have to treat non-DL things differently.

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6179
  • Yes Pinky, Do-more will control the world!
Re: Data from (2) DL06's to a Do-More
« Reply #7 on: November 25, 2013, 04:15:15 PM »
I take it back. MRX is more flexible anyway. I don't have to treat non-DL things differently.

DLRX/WX is just the Do-more-ification of DL's RX/WX, and as you note, is pretty much useless outside of legacy DL controllers. The big benefit is that it eliminates the need for Modbus mappings of DL (e.g. V100 == V100), but not much else.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

CReese

  • Hero Member
  • *****
  • Posts: 184
Re: Data from (2) DL06's to a Do-More
« Reply #8 on: November 25, 2013, 04:18:57 PM »
Yeah, but as soon as you know a beginning address, it's all offset. It's a PIA to get there, but once you're there, you're there.

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6179
  • Yes Pinky, Do-more will control the world!
Re: Data from (2) DL06's to a Do-More
« Reply #9 on: November 25, 2013, 04:19:56 PM »
Yeah, but as soon as you know a beginning address, it's all offset. It's a PIA to get there, but once you're there, you're there.

Agreed.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

Controls Guy

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 3628
  • Darth Ladder
Re: Data from (2) DL06's to a Do-More
« Reply #10 on: November 26, 2013, 04:02:46 PM »
And even the address translation is barely that, at least for VMems.  It's just an octal-decimal conversion, and Excel (and maybe your phone) already have that built in.
I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.