« on: February 07, 2013, 08:58:57 PM »
I have a problem with the CTRIO2 and limits.  I have limits wired to 1C and 1D, with the direction bit off, the motor slows down to creep speed, then stops at limit 2.  If the direction bit is On, the 1st limit is not seen, but the motor will stop at the second limit.  Folks at Automation Direct tell me they've reported the issue.  Can someone tell me when it will be fixed?  Just wondering if I need to ship everything back, and get a refund while I still can.

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6174
  • Yes Pinky, Do-more will control the world!
Re: Do-More CTAXLMT Bug?
« Reply #1 on: February 08, 2013, 12:53:34 AM »
It's a minor bug in the CTRIO2. It actually does 'see' the first limit, but doesn't properly decel in the reverse direction. The firmware was fixed yesterday, but we wanted to test it a bit before we release it. We'll be posting it shortly.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

Voltorb

  • Newbie
  • *
  • Posts: 2
Re: Do-More CTAXLMT Bug?
« Reply #2 on: February 08, 2013, 07:25:52 AM »
That's EXCELLENT news!  Thank you!