No I hadn't heard anything so just figured i would keep moving forward with the BRX upgrades.
We are upgrading one of the other PLC's that this one communicates with to BRX and are going to switch over tomorrow. I figured I would see if the problems went away after that.
I have had 3 more watchdogs since my last posting but we have been doing a lot more communication with the old DirectLogic PLC to the new BRX we are installing in it's place so that might point to it be a communication issue.
If it doesn't get better after that I'll keep trying to figure out how to duplicate it or see if i can isolate the issue to a specific section of code.
The DST411 ($DebugTrapAddr) is still 0 so probably something in the cabinet or bad Ethernet comms.
Thanks,
John.
One of the things we added is more debug information for troubleshooting a reboot caused by comms.
So, with what other things is it talking?
In Data View you can check out DST72 ($FreePackets). Its value should hover around 375. If it starts trending downward, turn ON ST300. This causes memory to fill with connection data (DST98-399 will now contain data of what is using sessions).
Also, if you turn ON ST301, then it will put data into DST200-205. These values can be helpful to us as well.