Author Topic: BRX RTD BX-06RTD error in EIO  (Read 6582 times)

MikeR

  • Full Member
  • ***
  • Posts: 24
BRX RTD BX-06RTD error in EIO
« on: December 15, 2019, 02:10:23 PM »
I have a BX-06RTD Local I/O with only 3 channels enabled that works fine. i have the same module/config/wiring EIO on a BX-DMIO in the same system that i can't seem to stop getting channel out of range on channel 5 and channel burned out on 4 and 6. all unused inputs are connected to common.

I've checked wiring, tried forcing config, power-cycle, and changing config to different settings. it's not causing a problem for me, i just don't like seeing it.

Thanks

ADC Product Engineer

  • Hero Member
  • *****
  • Posts: 270
Re: BRX RTD BX-06RTD error in EIO
« Reply #1 on: December 16, 2019, 07:42:47 AM »
Check the last two digits of the serial number.  It should be A2 or greater.  If it is A1, please do an RMA at AutomationDirect.com.

https://www.automationdirect.com/adc/return/return

MikeR

  • Full Member
  • ***
  • Posts: 24
Re: BRX RTD BX-06RTD error in EIO
« Reply #2 on: December 16, 2019, 04:29:17 PM »
i don't plan to be at that site for about a month. I ordered these modules on 10/15. if this module is the prev. version, is this the only known issue?

ADC Product Engineer

  • Hero Member
  • *****
  • Posts: 270
Re: BRX RTD BX-06RTD error in EIO
« Reply #3 on: December 17, 2019, 07:34:19 AM »
As far as I am aware.