Author Topic: Set up a Modbus Server on H2-DM1E PLC  (Read 11161 times)

Stan

  • Newbie
  • *
  • Posts: 8
Set up a Modbus Server on H2-DM1E PLC
« on: June 09, 2014, 03:51:58 PM »
I need to set up a modbus server on a Do-More PLC but I'm having trouble finding information on how to do this.  Can anyone point me to a tuitorial or FAQ that explains how to do this?

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6175
  • Yes Pinky, Do-more will control the world!
Re: Set up a Modbus Server on H2-DM1E PLC
« Reply #1 on: June 09, 2014, 05:01:00 PM »
What device? Serial or Ethernet?
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

Stan

  • Newbie
  • *
  • Posts: 8
Re: Set up a Modbus Server on H2-DM1E PLC
« Reply #2 on: June 10, 2014, 07:04:45 AM »
I'm trying to do this using ethernet. 

MikeS

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 270
    • Host Engineering, Inc.
Re: Set up a Modbus Server on H2-DM1E PLC
« Reply #3 on: June 10, 2014, 08:13:26 AM »
the on-board Ethernet port of the DM1E CPU comes preconfigured with the Modbus/TCP server enabled. You can see and modify this configuration on the CPU page of the System Configuration.
Good design costs a lot. Bad design costs even more.