General Category => EBCs and EBC100s => Topic started by: duvals on August 22, 2012, 03:37:36 PM

Title: Field I/O RTD input Module
Post by: duvals on August 22, 2012, 03:37:36 PM
I'm unable to configure the module. My setup is:
Main PLC D2-260 with module H2-ERM

Slave: T1H-EBC100, T1F-16RTD.

I use the ERM Workbench to configure the module with the default configuration and mapping.

I use the latest firmware in all module.

Does someone have already use this config???
Title: Re: Field I/O RTD input Module
Post by: Greg on August 22, 2012, 04:35:51 PM
What setup are you wanting to do? The RTD types are set by jumpers on the T1F-16RTD module.
Input word 1-2 = Ch1
Input word 3-4 = Ch2
.
.
.
Input word 29-30 = Ch15
Input word 31-32 = Ch16

Or do you mean ERM Workbench gets an error when trying to write the configuration to the ERM? If so, what is the error?