Host Engineering Forum
General Category => General Discussion => Topic started by: gk77 on May 22, 2012, 11:23:34 AM
-
We are looking to update some test equipment that should have been done long ago. The machine is rather simple, acuating an air cylinder to open and close a drawer. What we would like to do monitor the force with a load cell for opening AND closing the drawer and then define parameters for failures. The problem I think i have is that when pulling the drawer open, i get a + voltage from my load cell, and when i push the drawer closed i get a - voltage.
All the cards i see for the DL06 are 0-5, 0-10... voltages. How do i see and translate a negative voltage input. I idn't see anything searching the forum.
And yes, i am fairly new, but have successfully programmed a few machines so far with much success with pressure transducers and running 5 station test systems all with Cmore panels.
-
Make sure you have a load cell amplifier. Most provide an offset adjustment. Move the offset so that zero signal gives you a positive signal. Ensure that the worst negative doesn't drive the signal below zero. You should them be able to handle the math in the PLC.