I am working on set up of my H2-CTRIO in a DL205 PLC with a DL250-1 CPU slot #1 I am using the post that Greg the moderator wrote on October 31, 2008, at 04:48:10 pm ยป ( How do you program a Stepper with encoder for feedback. )
and I am not getting the same range for the Word OUTPUT range Start is at V2030 My range is V2030-V2053 ??
not the V2030-V2061 as described in this post as well as the manual...
What is going on ??
-
Check that you have the latest version of CTRIO Workbench. The latest one allocated more input and oputput space.
-
b_carlton
Yep as always you are Correct !!!
updated and now I get the proper range on the outputs