Title: E401 no END
Post by: Dr Royce Mitchell on May 03, 2012, 11:29:55 AM
I have a problem that I have been unable to solve. I have an END statement in my DL06 program but am getting a fatal error indication in the DirectSoft software program saying that I don't have an END statement.

Does anyone know why that might be?
Title: Re: E401 no END
Post by: Greg on May 03, 2012, 04:07:04 PM
Have you accepted the END statement in DirectSOFT (press F8 while in the Editor) and downloaded it to the PLC yet?

If so, then, you might want to just clear the PLC, clear scratchpad memory and try downloading the project again.