I am using a flow sensor with the H0-CTRIO and a DL06. Everytime I am doing a soft reset the" at reset value" stay on (green) and will not go off.
Anyone have a clue off what is going on?
I previously did the same application with a DL260 and the H2-CTRIO without any problem.
Thanks everyone for any suggestion.
???
-
laurent, in order to help you with this, I need a bit more detail as to what you are saying. I started to answer you but found that I was making numerous assumptions. Questions:
- Does the flow sensor keep counting after you do the soft reset?
- Is the flow sensor a quadrature encoder?
- Is the CTRIO configured for quadrature counter?
- Is this CTRIO input scaled?
- If so, how?
- Are you running a Preset Table that may reset the count?
- Are you explaning this issue from a point of view of being in CTRIO Workbench's Monitor I/O function?
- If using Monitor I/O, how did you answer the question "Would you like me to suspend output reads?"?
- If using Monitor I/O, is the DL06 program possibly writing over the Reset bit?
- If using Monitor I/O, is the DL06 program possibly writing over the Count?
-
I found my problem, I had to load k0 in my reset register after I did turned my bit on.
Thanks for your response!
:D