Title: DL405 - What is the addressing scheme for analog inputs and outputs?
Post by: wildcatherder on August 28, 2009, 01:33:21 PM
I've been working with discrete inputs and outputs and now have to use analog.  I have looked EVERYWHERE and cannot find the answer to this simple question.

What are the memory addresses for the analog inputs for a 16-point module (D4-16ND2F) in the first (leftmost) slot of a DL405?

I find information that addresses in the first slot begin at V40400 but it is not clear how much address space each input requires.
I have seen examples that show an 8-point analog current module using only eight addresses and referred to as X0 through X7.

How can X0 be the same address for a 1-bit digital input OR a 12-bit analog input?

I also find references to "pointer method".  I know what pointers are but I cannot find an explicit definition of how this applies to DirectSoft5 programming.

I found the Analog_IBox_Help_Example.PRJ but it starts with using ANLGIN Analog Input Module Pointer Setup which does not appear on the list of available IBoxes for my version of DirectSoft5 v5.3.

Please help.
Title: Re: DL405 - What is the addressing scheme for analog inputs and outputs?
Post by: b_carlton on August 28, 2009, 02:04:59 PM
D4-16ND2F is NOT an analog input card. It is a 16 point DC discrete input card.
Title: Re: DL405 - What is the addressing scheme for analog inputs and outputs?
Post by: MikeS on August 28, 2009, 02:28:09 PM
essentially what is happening is that the analog modules multiplex all of their channels into one 16-bit register. So the PLC needs ladder logic to read this one location and de-multiplex it into the PLC's v-memory. you'll find the appropriate ladder logic for each module in the analog i/o user manual, there's a chapter devoted to each analog module (by part number).

the ibox you referred to is only available for the DL205 series PLCs, not the dl405 series. so it's not a limitation of DSOFT v5.3, it's just not appropriate for your particular PLC.