It seems we found a bug where we had a project on the 36CH BRX and then changed the PLC type to the 18CH BRX. In the old configuration (36CH) we had the configuration to do the scaling on WX0-WX3 to RX0-RX3. On the new configuration (18CH) we added a BX-08UT mapped to WX1-WX8 and scaled to RX1-RX8 using the RTD config. The RX1-RX3 continued to be scaled to the old configuration no matter what we did until we changed the project PLC type back to the (36CH) then we could disable analog scaling on WX1-WX3 and then change the PLC type back to the 18CH and then the scaling on the BX-08UT worked as expected.