General Category => Do-more CPUs and Do-more Designer Software => Topic started by: Saturn_Europa1 on February 13, 2024, 05:04:41 AM
-
I have a Do-More PLC controlling 6 GS-2 drives through GS-EDRV100s. The PLC has a H2-ECOM100 ethernet module and the CPU is a H2-DM1E.
The Do-More software is v2.4. I am not sure of the exact firmware in the PLC.
The PLC controls the speed on the drives through the GS-EDRV100s. The speed inputs to the PLC is done through a C-More EA9 8" touch screen. Once in a while the speed on the drives will not update. I will enter the desired speed, the set point on the C-More will change but the drives will not respond to the new speed set point.
Any idea of what could be causing this?
-
I forgot to add that the only solution I have found is cycling power to the PLC. When you cycle power to the PLC it also cycles power to the C-mores and the GS-EDVR100s.
I tried cycling power to the the GS-EDVR100s alone but this did not fix the problem.
-
At the very least I'd get the PLC to the latest firmware. Current is 2.9.8 and we are releasing 2.9.9 shortly.
-
Someone told me not to do an update because we would lose communication with the C-Mores and the ethernet network. This doesnt make sense to me. Have you heard of anything like this?
-
Someone told me not to do an update because we would lose communication with the C-Mores and the ethernet network. This doesnt make sense to me. Have you heard of anything like this?
No clue why that would be.
-
Someone told me not to do an update because we would lose communication with the C-Mores and the ethernet network. This doesnt make sense to me. Have you heard of anything like this?
You are going to get a pause while the controller is updating, but that is all. I suppose if you are using the GS-EDRV100's as remote control you might get a reset depending on your settings, but it will pick back up. I wouldn't do it while you are running anything major, but that's just me.