I am using a D2-262 CPU and a Red Lion ZCH0500 incremental encoder (quadrature) with an HMI. My question is about the counter: I can use an UP/DOWN COUNTER (UDC) to do what I need, but the encoder has 500 pulses per revolution and I am overwhelming my counter. It begins to miss some pulses at about 5 rpm. I need the resolution of the 500 pulses.
My question is: must I use an H0 or H2-CTRIO2? These modules are expensive, I thought there might be a built-in Highspeed Counter.
Have a great Day! -Sarcio
-
Look at the D2-CTRINT
https://www.automationdirect.com/adc/shopping/catalog/programmable_controllers/directlogic_plcs_(micro_to_small,_brick_-a-_modular)/motion_-a-_specialty_modules/d2-ctrint
You might have been thinking of the BRX Do-more PLCs. Many of them have built-in HSIO.
*** EDIT ***
It MUST go into the first slot next to the CPU
-
You might have been thinking of the BRX Do-more PLCs. Many of them have built-in HSIO
I was actually thinking of the Panasonic FP-XH C60RD unit. It has a built-in highspeed counter. I decided to go with Automation Direct because of the controls I inherited and I wanted to keep everything the same. Oh well.
Look at the D2-CTRINT
I will probably go with the H2-CTRIO2 because I have six quadrature encoders and I need to have a preset for each. The H2 can handle 2 quadrature encoders instead of just one and space is at a premium.
Thanks for the input.
-
I will probably go with the H2-CTRIO2 because I have six quadrature encoders and I need to have a preset for each. The H2 can handle 2 quadrature encoders instead of just one and space is at a premium.
Thanks for the input.
Good choice!
-
BTW, the D2-CTRINT is NOT supported with the D2-262.
-
Thanks for the heads up.