General Category => Do-more CPUs and Do-more Designer Software => Topic started by: Controls Guy on September 22, 2023, 02:34:05 PM
-
I have a program that has Modbus remote I/O configured and can be used with either native (local) I/O or the Modbus distributed I/O with no program mod or configuration. I solve the logic to Y32-Ynnn and use that as the source for the Modbus slave devices. Whichever is hooked up gets the the data and the program doesn't care. Now I want to do something if and only if I'm using Modbus slaves but I'd like not to have anything to have to configure in the program so I don't forget to do it while commissioning (Old timer's disease). Is there a way for the program to read what I/O is installed locally, so if not I can do the thing?
-
HWINFO can read a base/slot's module ID. I/O counts too. Coming soon, I/O addresses.
-
Awesome, thx! I was also thinking of looking for no change in .XferCount on the relevant MTCP I/O node, but only enabling the watchdog for that on having .XferCount be >50 or something. At native sites, .XferCount should be 0, so it would disable the watchdog.