Host Engineering Forum

General Category => EBCs and EBC100s => Topic started by: Dmdtrain on September 08, 2023, 12:38:50 PM

Title: EBCs erroring frequently
Post by: Dmdtrain on September 08, 2023, 12:38:50 PM
Hello,

We have quite a few T1H-EBCs and EBC100s. It seems to be more of an issue with the non 100s though it has happened with them as well. When our lines start up we sequence turning on the conveyors thru a counter and often after 4-6 conveyors turn on we will get an IO fault shutting the system back down.

We haven't been able to find a true solution for this. Sometimes we'll swap parts and it'll work again, sometimes a power cycle fixes it, sometimes just letting it sit for a few minutes will.

Does anyone have any suggestions on why this could be happening?

Thank you.
Title: Re: EBCs erroring frequently
Post by: Greg on September 12, 2023, 09:41:17 AM
Do the T1H-EBC/EBC100s have lots of I/O? Or like relay output modules, or long strings of double-wide I/O modules?
Title: Re: EBCs erroring frequently
Post by: Dmdtrain on September 18, 2023, 10:12:37 AM
Do the T1H-EBC/EBC100s have lots of I/O? Or like relay output modules, or long strings of double-wide I/O modules?

It varies from panel to panel. All digital in/out(s). 24-48 would be about the median range on any given panel with some with less and some with more. In/Out(s) accounting for 50% each.
Title: Re: EBCs erroring frequently
Post by: Greg on September 18, 2023, 03:10:30 PM
Do the T1H-EBC/EBC100s have lots of I/O? Or like relay output modules, or long strings of double-wide I/O modules?
...24-48 would be about the median range on any given panel with some with less and some with more. In/Out(s) accounting for 50% each.
24-48 what? Modules? I/O points? Also, are most/any of them double-wide modules? And, again, are these relay modules?

The reason I'm asking this:
All these things add up (are cumulative) where noise is concerned. Anything done to counter any of the above list should improve the reliability of your I/O.