I'm troubleshooting an issue with some Stride I/O modules where the ethernet port on those devices is occasionally unable to pass traffic after bootup on my network. It happens about 50% of the time, so it's been fairly easy to troubleshoot.
I think I've isolated the problem to being related to a Ruckus Wireless Access point on the same LAN. Whenever I disconnect this device, the Stride units boot up properly. The network has quite a few other devices on it, including 3 BRX PLCs.
In the course of troubleshooting, I was reviewing Wireshark captures and noticed that there's periodic ICMP traffic initiated by 2 of the BRX PLCs to the WiFi access point, and I can't figure out what's causing this. The 2 BRX units have a very basic setup and are mainly in place as slave devices using PeerLink to transfer data back to the master PLC.
See attached pic for a screenshot of the Wireshark capture. The PCAP is here: https://www.dropbox.com/s/frrubass43q2ok0/BRX%20Wireshark.pcapng?dl=0
Any ideas?
Thanks.
-
The PLCs are responding to packet #9 indicating that they can't route it. They received the packet because it was sent to the subnet broadcast address of their subnet.
-
Ah ok. I knew it was sent to the subnet broadcast address, but I didn't realize that would cause a response. I haven't seen that behavior from other devices... In any case, it certainly shouldn't be causing any problems.
Thanks for the quick reply as always - much appreciated!