Host Engineering Forum
General Category => DirectSOFT => Topic started by: rlawson on May 15, 2007, 06:17:02 AM
-
I have a heat treating process where I want to use the ramp soak generator with a 260 cpu system. The problem that I have is the ramping counts per second function. For example I need to ramp at a rate of 100 deg F per hour. With the ramp slope variable I am limited from 00.00 to 99.99 counts per second. 100 deg per hour equates to .0277. .01 gives me 36 deg F per hour, .02 gives 72 deg/hr, and .03 gives 108. Since I need to maintain 100 degrees instead of 72 or 108, what are my options? Is this beyone the capabitity of the built in ramp soak generator?
Tks, Robert
-
That's all you have to work with in these PLCs.
You'll have to roll your own ramp/soak table in your ladder code to get the steps you need.
-
Thats what I figured, thanks for confirming what I suspected.
Robert
-
Sound like a good feature for a future PLC...ramp/soak generator with selectable time base... ;)