In the shown photo I've got a TC reading ambient temperature. When I change the .SP to slightly below the current ambient temp, the forward acting loop is still giving slight output with 0 Rate and 0 Reset. Why is this? I would expect that by setting the setpoint to anything lower than the current .PV would yield zero output from the loop. What am I missing?
-
The Bias term is non-zero, hence it is affecting the .Output calculation. The Bias can become non-zero based on your "bumpless" transition behavior option or previous tuning constants.
-
What's the likelihood of adding a tickbox that would keep (force) the bias term at zero on a manual/auto transition? For many of the ways I would use the PID, it would be nice to keep it at zero during a transition. Not sure if this would be useful or not to the general user base. For now I'll just one shot the bias term to zero during the transition.
-
I was thinking sort of the same thing. If Ki is set to zero (at least from Do-More), maybe clear bias by default?
-
Not continuously keep it at zero, just one-shot if the user clears Ki.
-
What's the likelihood of adding a tickbox that would keep (force) the bias term at zero on a manual/auto transition? For many of the ways I would use the PID, it would be nice to keep it at zero during a transition. Not sure if this would be useful or not to the general user base. For now I'll just one shot the bias term to zero during the transition.
This is a fairly common issue. If Mark/Bob can do add a tickbox or a structure field to force bias to zero, I would lend it my vote.