General Category => Do-more CPUs and Do-more Designer Software => Topic started by: Joe Hance on May 31, 2020, 09:21:24 AM

Title: Weintek cmt-SVR-200 to BRX Ethernet
Post by: Joe Hance on May 31, 2020, 09:21:24 AM
We are trying to connect a Weintek cmt-SVR-200 using Ethernet connection to a BRX.  Not having any luck.
We've setup a Modbus/TCP Ethernet device in EB, entered the IP address.  We can get it to ping.
Title: Re: Weintek cmt-SVR-200 to BRX Ethernet
Post by: ADC Product Engineer on May 31, 2020, 10:05:32 AM
Wow the documentation is light on that thing.   Looks like the Weintek wants to be the master.  Nothing to do in the PLC other than put the data in the appropriate MI, MC, MIR, MHR addresses.

https://forum.weintek.com/l3-set-a-connection-with-plc/
Title: Re: Weintek cmt-SVR-200 to BRX Ethernet
Post by: Joe Hance on May 31, 2020, 11:54:20 AM
Thank you for the reply and the link.  We'll give it a whirl.