Hi everybody,
Can I use Terminator I/O with DL06 PLC?
If yes, then how to access I/O's?.
Best regards.
Chiali.
-
You could with the MODBUS communication interface. Standard MODBUS commands from the DL06 2dn port would be used. Check to see if all interface modules can be used.
-
Chiali,
Also, if you use the T1H-EBC100 in the Terminator I/O, then you could also use an H0-ECOM100 in the DL06. The H0-ECOM100 can be the Modbus TCP Master and the T1H-EBC100 can be the Modbus TCP Slave.
-
Thank you all for your responses.
I would like to know how to address the inputs and the outputs in both cases.
-
If you use the H0-ECOM100 and the Modbus TCP option then you would:
- Define Modbus TCP peer-to-peer configuration (using NetEdit) for your H0-ECOM100.
- Use NetEdit to view the Base Contents of the T1H-EBC100 that is to be the slave. This also lists the Modbus TCP Addressing for the I/O plugged into the T1H-EBC100.
- Use RX/WX (or IBox equivalents) in ladder logic to read/write to the T1H-EBC100 I/O.
- Modbus TCP addressing (for the RX/WX) is defined in this document: http://www.hosteng.com/FAQFiles/ECOM100%20Server%20Client%20Mapping.pdf.
Hope that helps!