General Category => General Discussion => Topic started by: chiali on October 19, 2008, 11:48:23 AM

Title: Terminator I/O.
Post by: chiali on October 19, 2008, 11:48:23 AM
Hi everybody,

Can I use Terminator I/O with DL06 PLC?
If yes, then how to access I/O's?.

Best regards.

Chiali.
Title: Re: Terminator I/O.
Post by: b_carlton on October 19, 2008, 01:56:15 PM
You could with the MODBUS communication interface. Standard MODBUS commands from the DL06 2dn port would be used. Check to see if all interface modules can be used.
Title: Re: Terminator I/O.
Post by: Greg on October 20, 2008, 09:02:53 AM
Chiali,

Also, if you use the T1H-EBC100 in the Terminator I/O, then you could also use an H0-ECOM100 in the DL06. The H0-ECOM100 can be the Modbus TCP Master and the T1H-EBC100 can be the Modbus TCP Slave.
Title: Re: Terminator I/O.
Post by: chiali on October 20, 2008, 09:33:06 AM
Thank you all for your responses.

I would like to know how to address the inputs and the outputs in both cases.
Title: Re: Terminator I/O.
Post by: Greg on October 20, 2008, 09:56:54 AM
If you use the H0-ECOM100 and the Modbus TCP option then you would:

Hope that helps!